I am having a Intertherm 012H 240v electric furnace installed. The installer asked me which wiring system would i prefer. The manual offers a choice:
A.) Single @ 51.2 total amperes with a max over-current rating of 70 (which i believe requires #4 wire
B.) Dual "A"/Dual "B" Single A is 27.1, max over is 40, Single B is 24.2, max over is 30.
My questions are:
-
Which is best Single or Dual? One big 70 amp breaker with big fat, hard to bend wire, or Dual, with separate breakers and easy to use wire?
-
If dual, if one circuit pops (either a or b) will the furnace continue to operate.
-
Would i be correct to assume that either method would need 4 wire? Sinfle being #4/4 wire. And Dual A #8/4 wire. Dual B #10/4 wire
Thanks to all those who reply. Bruce
Best Answer
Use the dual breaker method -- whoever wrote the manual needs a Code-slap with 424.22(B), as the single breaker method doesn't comply with it.
If you're short slots -- use a double-stuff (quadruplex) breaker.