I have a double pole 30 amp breaker controlling a 230 volt load that I need to replace. I cannot obtain one at this moment; perhaps tomorrow but maybe next week.

Either way, I have two good used 30 amp breakers that I could put in place of the 30 amp double pole.

Will it be okay for me to do this if I take the tie bar off of the old breaker and re-use it?

I have already pulled the tie bar off and have the two breakers ready to go. Hoping that this will be okay!

Best Answer

For this to work, the two single breakers must pull power off each bus leg to give you 240VAC. If they pull off the same leg, you only get 120VAC (parallel feed). Check to make sure they use alternate bus connections when they're side-by-side.