The best solution here, would be to find a UL approved device that can satisfy your needs. Building your own device can be risky, and fraught with unexpected dangers. There are tons of UL approved power strips available on the market, it hard to imagine you wouldn't be able to find one that suits your needs.
If you must build your own solution, you'll want to be aware of at least a few of the dangers.
Exposed wiring
First and foremost, you'll want to make sure nobody can ever touch anything that could be energized. This means that all connections, splices, junction, etc. should be contained within an enclosure. You'll also want to make sure the enclosure is listed for the use, so that it will also contain any sparks, heat, etc. that might be produced.
Most areas now require tamper resistant receptacles in living spaces (living rooms, bedrooms, dining rooms, etc.), so you'll likely want to use TR receptacles for this project.
Overcurrent
While there are no hard-and-fast limits on the number of receptacles on a circuit, or the number of devices that can be fed by a receptacle. You'll want to be cautious not to overload your wiring. In industrial and commercial settings, 180 Volt-Amperes is the value that's used to calculate receptacle loads. If you use this as a guide, you should have no problems with overloading the circuit.
While the circuit breaker should protect the house wiring, you may want to protect the wiring in your cabinet from overload as well. You can do this with a fuse, or circuit breaker. You'll want to wire this in as the first device, possibly putting it in the same enclosure as the watt meter.
Surge protection
Since you'll be dealing with expensive electronics, you'll probably want some form of surge protection. There are receptacles available that offer surge protection built in, but they may not offer the level of protection you require, or that can be found in a manufactured surge strip.
It is not controlled by a switch and I didn’t break any tabs.
What could make this happen?
- Debris inside the socket of the ground conductor
- A defectively manufactured outlet
Is it safe to use the outlet or just the bottom of the duplex?
Safety is a relative thing.
If you use the ungrounded top outlet it will be as safe as older houses that were built before grounding was a thing, and were considered safe in their time. It will also make no difference for two prong appliances.
If you crazyglue an outlet protector over the top outlet to prevent use of the top outlet, then it will be as safe as not using it.
But maybe the DC converter will short to hot and electrify the phone someone is holding up to their head.
I say take it back to the store and report the fault and get an exchange.
You got a product that is less than it should be. Safety or not, you'd return a plasma tv if it had lines down it or only received even channels. Return this outlet too.
Do outlets with USB ports show open grounds?
Only busted ones.
would putting a GFI outlet in that box assure it is grounded?
Nope. GFCIs do not create ground.
Changing the part out (with a gfci, or with any other outlet) would most likely solve the problem though. And in a kid's room, I think a GFCI is worth more than USB outlets if its a kid you want to keep.
Perhaps consider installing one GFCI in the "first" outlet box in that room, or in what ever the next closest junction before the circuit enters that room. Then USB outlets inside the room. In 60 seconds of Googling, I could not find an outlet that had GFCI and USB in one. You could also use a GFCI breaker but those are a pain in the neck.
something I may be missing
The receipt for that usb outlet, and its original packaging? With that, you should be all set. Let the clerk know it is dangerously faulty so they think longer before re-shelving it. If you get another of the same model and it has another fault, then you should tell us what model it is so it can be avoided. Good on you for testing the outlets after installing. I haven't done that on nema 5's in a while....
Best Answer
We have a FAQ for novices doing receptacles.
There are many tricks and traps when changing receptacles. I wrote a Q&A specifically for folks like you, please review it.
The #1 thing I'd say that isn't mentioned there is don't downgrade an outlet from GFCI to USB (unless it's redundant).
Speaking of testing, those 3-lamp testers have 3 Rather Useful lights which let you do three tests at once. (Obviously, if any lights light, the outlet is most likely hot; but that is not enough.) But the little chart/legend is completely wrong; it's about as useful as a "magic 8-ball". It's actually optimized for new construction; once built, houses have different kinds of problems.
As far as safety, once you're opening things up, turn the entire house off and check it by plugging a lamp into both outlets. There are so many surprises and gotchas for the novice (MWBC, borrowed neutrals, you name it) that it's not worth fooling around any other way. It's what I do myself in our factory building; I pull the main 480V which shuts off all the 120/240V transformers.