Electrical – Run conduit perpendicular to ceiling joists in garage

conduitelectricaljoistswiring

I have a sub panel on a finished wall in my garage. I want to add two 20 amp circuits and run them go outlets on two unfinished walls on the sides of the garage.

Is it okay to run metal conduit across the joists above? Does it have to be run along a board or attached to a joist every so far?

Where the conduit reached the inside of the wall, can I run without conduit inside the walls? I plan to finish the garage walls after.

enter image description here
enter image description here
enter image description here
enter image description hereenter image description hereenter image description here

Best Answer

I would come out the right side instead of the bottom, and stick with a surface conduit run

Given your situation (a NEMA 3R box surface-mounted indoors), I would use a nipple and suitable conduit body (it'll be either an LL or an LR, as you want the cover to face out towards you) to come up into a conduit run along the wall surface, then use a prefab sweep to transition to the run across/along the ceiling joists, supporting within 3' of termination points and at 10' or shorter intervals otherwise (if you don't want to spend time figuring it out, it may be easier just to strap it down to every joist it crosses). This saves you the hassle of trying to get wires into the back of a surface-mounted box, as well as the need to use a junction box to transition between wiring methods.

Inside this, you'll want to use individual 12AWG stranded THHNs (2 hots and a neutral, forming a multi-wire branch circuit or MWBC with the metal conduit as the equipment grounding path) to the various outlets, with a GFTCB220 in the subpanel providing protection to it all, given that your subpanel appears to take type BR breakers, and is configured in a way that you can add breakers to it without causing issues with the Code rules surrounding your solar setup. Make sure to use a torque screwdriver to torque the breaker and busbar screws on the panel to spec, by the way! (It doesn't hurt to use it on receptacles, for that matter.)

P.S. if you're wondering why I called out wiring the setup as a MWBC instead of as two separate 120V branch circuits, using a MWBC here gives you the ability to get both 120 and 240V out of the circuit, which is helpful for running power tools or other such high-demand loads.