I am removing two 15 amp breakers at the top left of my 40 space electric panel to be replaced with a 2 pole 30 amp breaker for backup generator. Can I just run two THHN #14 wires through a flexible conduit from an adjacent sub-feed panel and use common ground and neutral on first 40 space panel?
Electrical – run wires for neutral and ground separate from the feeds for a new sub-panel
electrical-panel
Related Topic
- Electrical – Main service electric panel has no neutral wire – both neutral and ground wires on same bar – sub panel question
- Electrical – Separating neutral and ground in panel
- Electrical – Confirming the Setup and Wiring of 60AMP Subpanel
- Electrical – Is Sub-panel Ground and Neutral Connected to Main Ground and Neutral Bar?
- Electrical – put the sub-panel for the attached garage in the attic
- EV Charger Wiring – Can 2 Wires Be Run from a 2 Pole Breaker to a Single Slot on an EV Charger?
- Electrical – Am I correctly replacing 2 x two-pole breakers with a quadraplex breaker
- Electrical – use TC-ER Cu Awg 4-3 THHN for a shed sub-panel
Best Answer
Ground yes. Neutral no.
You can do that with safety ground.
You cannot do that with neutral. Neutral needs to come over to the new panel that the hots are served out of.
This is easier to justify when using a type of metal conduit which itself is a valid grounding path, which is typically NOT the flexible kinds. EMT is a little more work but takes care of the grounds for you.
There are also good reasons to try to keep inter-panel conduits shorter than 24". Otherwise you are only allowed 4 circuits in them and must significantly derate the large feeder if there are other circuits in the pipe.
There is nothing wrong with using a service panel as a junction box to hold the wire-nuts that extend the circuit. Note this is a NEC interpretation, that may not work in Canada.