Electrical – Running multiple 20A circuits to a shed

electricalshedwiring

I have an outdoor shed that was powered with a single 15A circuit by the previous homeowner. I'm trying to rewire it to carry three 20A circuits. It's about a 100' run from my main panel via 1/2" schedule 40 PVC. I would like to run (7) #12 THHN for 3 hots, 3 neutrals, and 1 shared ground. I would terminate at the shed with a subpanel, three 20a breakers and a ground rod. From what I understand, seven #12 wires should work fine in 1/2 schedule 40 PVC without derating. Am I missing anything or good to proceed? Alternatively if I only wanted two 20amp circuits, could I run a multiwire branched circuit with 2 hots on opposite phases, a shared neutral, and shared ground to a disconnect at the shed without worrying about a ground rod?

Best Answer

You can't parallel wires, or run a bunch of circuits between two buildings

It's illegal to parallel wires skinnier than 1/0 (NEC 310.10(H)), and also illegal to run more than one of the same kind of circuit (same voltage, similar/same usage) to an outbuilding as that violates NEC 225.30. So, both your original plans are of no use; practically speaking, this means you need to run a feeder to the outbuilding, and fit a subpanel there, as well as install grounding electrodes.

However, a feeder is your best plan anyway

Your proposal gives you 60A at 120V, and no 240V, at the shed. However, with a feeder, you can fit 50A at 240V down the same 1/2" PVC, with fewer wires, and more room for expansion at the subpanel. In particular, your 1/2" Schedule 40 PVC has 74mm2 of usable fill area, which is enough room for 2 8AWG stranded copper THHN hot wires, a 10AWG stranded copper THHN neutral, and a 10AWG bare stranded copper ground, for a total of 66mm2 of fill used. While this setup requires care with balancing the loads at the subpanel to avoid overloading the undersized neutral, it's the largest feeder that can be practically crammed into a 1/2" conduit without exceeding fill limits.

As to subpanel selection...

If you don't want to be changing panels out later, your best bet is to get the correct subpanel now, and that means not skimping out. You'll want a 100A or 125A, main breaker (to provide a shutoff at the shed), 24 or 30 space (note: space, not circuit) panel for this job; this provides plenty of room for future expansion, including 240V circuits. In fact, you're best off running your shop receptacle circuit as a 20A multi-wire branch circuit using a two-pole ground fault breaker; this provides you with easy access to 240V for power tools that want it. On top of this, you'll have a 120V circuit for the lights and a second 120V circuit for the window unit, at minimum.

...and grounding this

You will also need to fit a grounding electrode system at the shed; typically, a pair of 8' ground rods driven 8' apart and connected to each other and the subpanel ground bar with 8AWG bare copper wire will do the trick. Don't forget to pull the green bonding screw out of the subpanel and fit dedicated grounding bars to it while you're at it, though!

TORQUE ALL LUGS TO SPEC

Last but not least, you'll want to use an inch-pound torque wrench or torque screwdriver to tighten all breaker, busbar, and panel lug screws to their labeled specification torques. Not only is this a requirement of the 2017 NEC, found in 110.14(D), it's a good idea anyway, lest your electrical system give you the loose lugnut!