Electrical – Running power to an external building

cablingelectricalgarage

I'm thinking of running power to my garage, it's about 40 meters away (as the cable flies).

I've been researching and already know the best way to do this would be to run a cable from the house consumer unit to a consumer unit in the garage, and then run a ring of sockets and lighting on appropriate fuses.

My question is, if I ran steel armoured cable from a normal UK plug socket to the garage (no CU) and only run basic lighting and restrict my use of power tools (nothing too high load) would I get away with this simpler setup?

Basically treating this as a large extension cord.

For those interested, the reason I ask is because the solution would be semi-permanent, in that I would be able to remove it in the future. I can't bury the cable and as I don't own the house don't fancy messing with the consumer unit.

Best Answer

As this is, as you suggest, effectively a long extension cable, as long as you don't exceed the 13A maximum that you can draw from the single plug, there is little to stop you doing what you suggest (though it would be prudent to check that you will have enough "headroom" in your proposed cable in terms of voltage drop and earth loop impedance).

While you could run armoured cable, you might not want to. SWA can be pretty "uncooperative", although this is less of a problem at the cable sizes you are likely to need for a 13A load.

Personally, I'd give serious consideration to using some 2.5mm2 arctic grade flex rather than SWA, as it will be a lot more compliant to get it connected into the plug. (I'm guessing you'll need 2.5mm2 to meet the requirements for voltage drop over that distance and the earth loop impedance). Unless of course, you have particular concerns about damage to the cable.

For protection, it would also be worth making sure that the this is fed via an earth leakage circuit breaker, be it either in the plug, socket, or within your current consumer unit.