Electrical – safely chain lower rated receptacles from higher ones

electrical

I have a NEMA 10-50 receptacle wired properly.
I have a device with a NEMA 6-15 plug.

I think that I cannot chain a new NEMA 6-15 outlet from the existing 50amp service.

Is a plug adapter the appropriate choice here?

Best Answer

I was just looking into a related question and am on the NEC Article that does not allow you to chain a lower rated amperage receptacle from a higher rated one. NEC Table 210.21(B)(3) and its corresponding Article. States that if you have a 50A circuit then the device must also be rated 50A. In theory from a Code standpoint you could install a NEMA 6-15 on your circuit if you could find one that was rated to withstand 50A.

Good luck with that one.