I'm looking for the NEC code reference that allows a main panel within a home to contain a main breaker because the meter is directly on the other side of the outside wall, versus installing a meter-main outside. I remember hearing something to the effect of no more than 5 feet of service cable between the two boxes.

Best Answer

Article 230 Services

VI. Service Equipment — Disconnecting Means 230.70 General

Means shall be provided to disconnect all conductors in a building or other structure from the service-entrance conductors.

(A) Location.

The service disconnecting means shall be installed in accordance with 230.70(A)(1), (A)(2), and (A)(3).

(1) Readily Accessible Location.

The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.