This is an a double wide mobile home. The two sides of the kitchen are on different circuits. When both Breakers are on one side reads 120 hot to ground 120 neutral to ground 240 something hot to neutral. When just one breaker is on it reads 120v hot to ground nothing anywhere else
Electrical – see 240v between hot and neutral when one breaker is out in the mobile home
electrical
Related Topic
- Electrical – showing 50 volts between neutral and ground
- Electrical – How to determine why all the outlets in one room are out
- Electrical – Chinese Breaker Box (240v split-phase?) Lacks Neutral Wires and Grounding Bus
- Electrical – Why does one leg of the panel drop to 0v and the other rise to 240v when a load is connected
- Electrical – read 120v between the hots and neutral in a 240v circuit
- Electrical – Converting electric receptacle with one hot and two neutral wires to GFCI
- Electrical – Why would I have i lost one leg on 240 after maintenance guy changed 100 amp disconnect at the meter
Best Answer
Neutral to ground should not be 120. It should be at (or very near) 0. Neutral and ground are generally bonded at the service panel. When only one breaker being on causes this (and the other doesn't), it seems unlikely that you have lost your neutral service from the supplier. There is likely a fault on the neutral associated with one of the circuits. It's also possible that there is a faulty or mis-wired MWBC (explanation of MWBC here).
You could try disconnecting the wires from the breakers in the service panel and testing directly from the breaker to the neutral and ground. If everything tests as expected, you're looking at a wire fault. Otherwise, the wire isn't the first problem to fix.