Electrical – Service Entry Wire/Ground Location (100 amp service)

electrical

I am getting 100 amp service connected to my cabin (currently off grid). The power company wants me to install my meter base on the corner of the property, and for me to install 200' of underground conduit from the meter base pole to my cabin.

I plan to install a main panel on the meter pole, feeding a sub panel hung on the side of my cabin.

My question is, what type of wire should I use for the underground run? Also, do I need to ground the sub panel at the cabin as well?

Best Answer

You'll have to use a cable or wires that are rated for wet locations. You'll most likely use Underground Feeder (Type UF) cable, Underground Service-entrance cable (Type USE) , or THWN wires.

You'll have to install a proper grounding electrode at the cabin, and bond the grounding conductor to it.

You'll have a grounding electrode at the pole, where you'll bond the service neutral and the equipment grounding conductor. From there you'll run four wires (two "hots", one neutral, and one ground), and you'll keep the ground and neutral separate.