I tested my outlet and only had 85 volts on the black side and 24 volts on the white side why? There are several outlets on the same circuit that don't work with the same readings.I checked power in the panel bos it reads 120 volts at the black wire and the white wire reads none .
Electrical – several outlets dont work on same circuit
electrical
Related Topic
- Electrical – Why are some outlets still out after replacing an outlet
- Electrical – Problem with a circuit that has only 2 outlets, one is fed from breaker and that one feeds a 2nd outlet, 2nd is not working anymore
- Electrical – Replaced breaker, and still no power to outlets, but at circuit test 110
- Electrical – Connecting 120/240 receptacles on the same circuit breaker
- Electrical – Open Neutral Circuit yet all circuits outlets and wiring appear connected
- Smoke Detectors – Fixing Nonfunctional Lights on Same Circuit After Replacing Smoke Detector
- Electrical – Outlets/Lights out – Breaker on
Best Answer
You have a bad connection somewhere in the circuit. You'll have to pull apart the various junctions (outlets, switches, and fixtures) on this circuit to isolate the issue.
With the power turned off, disconnect the circuit somewhere that you suspect the issue to be located (unhook the load wires that go to the next junction). Outlets on the load side of that junction won't have any voltage when you turn the power back on. If the junction your testing had a low voltage issue, then you know that the issue isn't with any outlets that have no power with the load side disconnected. And if the junction your testing had the proper voltage, then the problem won't be with any junctions that still have power with the load side disconnected. Use this process of elimination to quickly narrow down which junctions could have a faulty connection.
You're simply trying to narrow down the problem in this chain, so here's an example:
breaker ---1---2---3---4X---5---6---7---
In the above, the numbers are your junctions on the circuit, and the X is your fault. Then:
The trick is that your junctions won't be numbered, so you just have to keep track of what works and what doesn't with each test. A sensitive non-contact voltage tester or stud finder with voltage sensitivity can help with tracing the circuit to find the most likely places for the bad connection.
As Tester101 would say, if you're at all uncertain, this is a good point for an electrician to help. One bad connection could indicate a lot of other issues from poor workmanship, and these issues are potential fire or electrocution hazards.