I was not working with this circuit breaker box but I was interested to see what was going on with only 3 breakers for the entire apartment. I found a neutral from the apartment going into the neutral with the power meter. Is this safe and to code? What else is wrong with this picture?
Electrical – Should a neutral wire ever be connected to the neutral for the power meter
electricalelectrical distributionwiring
Related Topic
- Electrical – Why would two circuit breakers be connected inside the service panel
- Electrical – Third Wire in 14-3 Wire Showing 50V When There Should be None
- Electrical – Subpanel – still getting power with breaker disconnected
- Electrical – Taking a neutral wire from another meter connection
- Electrical – Power everywhere after turning off the main circuit breaker
- Electrical – Are there any QO boxes with the neutral screws along the breakers like the Homeline
- Electrical Wiring Neutral Wire for Light Switch – Legal or Not?
- Electrical – Does code allow a main-lug-only panel connected to the meter lugs
Best Answer
I've labeled some things in your photo, that might help you understand what's going on.
The wires coming up into the panel are your service conductors, of which you have two "hot" and one "neutral". From there you have "hot" branch-circuit conductors, which are connected through circuit breakers. There's also a branch-circuit "neutral", for each branch circuit.
You seem to be concerned that one of the branch-circuit "neutral" conductors, is terminated under the same lug as the service "neutral". Which is a valid concern. You'd have to check the documentation or labeling on the panel, to determine how many conductors can be terminated at that terminal. National Electrical Code limits each terminal to one conductor, but allows device manufacturers to override that as long as there is documentation stating such.
It looks to me like that circuit predates the other two, and possibly even the panel itself. I'm guessing when they updated the panel, that conductor wouldn't physically reach the "neutral" bus. Instead of splicing the wire, they simply terminated it with the service "neutral".