My house has all of the GFCI outlets (approx 7 outlets/ 2 bathrooms, kitchen, and shed) running to a single GFCI breaker. Is this a proper setup for GFCI? I'm looking for a solution to keep the breaker from tripping when several devices are pulling power at once.
Electrical – Should all the home’s GFCI outlets be connected to a GFCI breaker
circuit breakerelectrical-panelgfci
Related Topic
- AFCI/GFCI Combo Breaker Trips Daily Under No Load
- Electrical – Miter saw tripping GFCI outlets
- Electrical – Tripping of generator GFCI 30amps breaker
- Installing GFCI outlets in multiwire branch circuit
- Electrical – Installing GFCI into a box that feeds two other outlets
- Electrical – All bathroom outlets are dead
- Electrical – Should I use a GFCI breaker or receptacles for the shed run
- Wiring – GFCI tester is tripping 15A breaker in panel; outlets on circuit do not appear to be GFCI outlets – is this a problem
Best Answer
No.
You should not put a GFCI outlet on a GCFI breaker. You need GFCI protection in only one device per circuit. Or stated better, you should not have a GFCI outlet downstream of a GFCI breaker. It's not unsafe per se, but it will be an unpredictable pain to deal with when it trips and you don't know where to go to reset it.
GFCI Outlets do not require GFCI breakers. GFCI Breakers make regular outlets and other devices GFCI protected.