I put in a 100 AMP sub panel from a 200 AMP service. The neutral and ground are separated in the sub panel. Would this bond the sub panel to the ground and neutral coming from service ground wire? I used 2-2-2-4 wire.

Best Answer

This is an example of a 100 amp Sub-panel coming off of a 200 amp Main-panel. Note the errors to current NEC code. Since there was an upgrade to the system, this one needed to be upgraded to current standards.

The ground had been connected to the neutral lug and the ground stake had also been connected to same. Also, note the horizontal bus connector bar.

(Believe it or not, the local electrical inspector missed this during remodeling with added circuits.)

Incorrect Sub-Panel Grounding

This shows the corrected connections in the same panel.

Correct Sub-Panel Grounding

This is the removed bar:

Removed bar