Electrical – Should I bond pipes to ground in detached building subpanel

electricalgrounding-and-bonding

In California.

My subpanel has a dedicated ground conductor run to it (ground and neutral bonded only at the main panel). The subpanel is in a building with its own plumbing, not connected to pipes where the main panel is located.

I know that I should not bond ground to neutral redundantly in the subpanel, but should I bond ground to plumbing independently from the subpanel?

My concern is that this will create an alternate path to ground.

Best Answer

You need to bond the subpanel ground bus to the plumbing

You will need to run a bonding conductor from the subpanel ground bus to a grounding clamp on the plumbing, as per NEC 250.104(A)(3):

(3) Multiple Buildings or Structures Supplied by a Feeder(s) or Branch Circuit(s). The metal water piping system(s) installed in or attached to a building or structure shall be bonded to any of the following:

(1) Building or structure disconnecting means enclosure where located at the building or structure

(2) Equipment grounding conductor run with the supply conductors

(3) One or more grounding electrodes used

The bonding jumper(s) shall be sized in accordance with Table 250.102(C)(1), based on the size of the feeder or branch-circuit conductors that supply the building or structure. The bonding jumper shall not be required to be larger than the largest ungrounded feeder or branch-circuit conductor supplying the building or structure.

This ensures that if the plumbing somehow became energized, the breaker would trip and disconnect the fault, instead of leaving the plumbing floating off to shocking voltages.

Don't worry about parallel paths here

As long as you have one and only one neutral-ground bond, located at the main service entrance, you are safe from parallel-path problems. Since ground wires don't normally carry current, they are free to run in parallel with each other, metal plumbing systems, metallic structural elements, and so on.