Electrical – Subpanel capacity

circuitelectricalelectrical-panelsubpanel

I will be installing a 125A subpanel using a #2 Cu THHN via 2" x 3"(L) conduit secured with four 2-in conduit locknuts (inside and outside of panels). The sub-panel shut-off will be a Q2125 125-Amp Double Pole Type QP.

The first photo shows the current configuration with a small, 8 circuit subpanel that will be replaced with a 20/20 125A box. I will further be adding 40A 240V (oven/micro combo), and 50A 240V (induction cooktop), as well as two 20A circuits, one for a dishwasher and another perhaps for an island outlet with beverage fridge (no sink or stove on the island).

I am trying to calculate the maximum capacity I can put on this subpanel, and whether I can just add the new circuits I mentioned above, or whether I need to rebalance with the main panel.

enter image description here
enter image description here

Best Answer

The trick is adding up the loads not the breakers you might have close to 200 double pole amps on a 125 amp panel and it could be ok but the size of the loads and the diversity of loads like heating / cooling all come into play but if you are putting in a new panel go big they don’t cost that much more.