It could have to do with the trip curves of the breakers, and/or the ambient temperature differences between panel locations.
Trip Curve
For example, let's say all the circuits on Phase A
are drawing 3 times the rated current. The trip curve for these breakers, say they will trip between 10 and 30 seconds at 3 times current. So the total current on Phase A
at the main panel is 270 amperes, or 2.7 times the rated current (100 A). The trip curve for the breaker in the main panel, says that it should trip between 12 and 35 seconds at 2.7 times current. If the breaker in the main panel is a bit more sensitive, you can see that it might actually trip before any of the secondary breakers.
Ambient Temperature
As well as a trip curve, circuit breakers will also have an ambient temperature curve. Breakers are designed and calibrated to operate at 40°C (104°F) ambient temperature. If the breaker is operated at an ambient temperature of -10°C to 24°C (14°F to 75°F), the breaker will be able to carry more current. However, if the breaker is operated at an ambient temperature between 41°C to 60°C (106°F to 140°F), it will carry less current and could lead to nuisance tripping.
For example, if the 100 ampere breaker is operating at 140°F ambient, you might find that it actually trips at only 85 amperes.
High Altitude
When breakers are installed at higher altitudes, the current has to be adjusted due to the reduced cooling effects of the thinner air. According to the documentation I could find, the adjustment multipliers are as follows:
- 0 - 6600 ft. (0 - 2011 m) -> 1
- 6600 - 8500 ft. (2011 - 2591 m) -> 0.99
- 8500 - 13000 ft. (2591 - 3962 m) -> 0.96
If you were installing a 100 ampere breaker at 10,000 ft., the breaker should only be expected to carry 96 amperes (100A * 0.96 = 96A
).
Though in your situation, the breakers are likely all installed at a similar altitude. So this it likely not the problem, unless the air near the main panel is significantly thinner for some other reason.
You could use one contact, two, or all three.
If using more than one, you could put them in parallel to reduce amperage through each one, which would increase service life (however if any stick "on", you cannot turn the device off). Or you could wire them in series for a higher capacity to interrupt voltage (but if any stick "off", you cannot turn the device on). The latter is a better fail-safe.
Best Answer
The 3 position switch Johnny pointed out is listed to UL 508 for industrial control devices, so it should be acceptable for switching some general-use receptacles around. (You'd be creating a tiny industrial control panel under Article 409 of the NEC -- your average junction box + cover combo meets NEMA 1, and there are provisions in the Code for an industrial control panel that's protected by the upstream breaker.)