Electrical – Taking power from double light switch to GFCI outlet

electricalgfciwiring

I am redoing some wiring in my bathroom. I have a vanity light on a single switch, a vent fan and ceiling light combo on a double switch and a GFCI outlet that are wired together in that order. It appears to me that these are all powered from one source coming from the panel, with 12/2 wires connecting them. Also at the end of the chain the GFCI is connected to two outdoor outlets.

I actually have managed to get everything working correctly except the GFCI outlet. I have power going to it but it keeps tripping. I got the power to the outlet by connecting the black wire leading to the GFCI to the top black screw on my light switch, that screw is hot whether or not the light or fan are turned on so it seemed to make sense. I took my common (white) wire and tied it in with the other white wires within the double switch box. I think that this is my problem as I am reading that you can't share common wires with GFCI. My question then would be what do I do with the common wire that will be powering the GFCI??? Or maybe that isn't my issue and my problem is something else?

Would love any help people can give. I am a newbie so be gentle. Everything in this series was previously working so I am hoping I can get it put back together without running new wires.

Best Answer

Your wiring should look something like this.

enter image description here

  1. You'll use a twist-on wire connector (or other approved means) to connect the incoming ungrounded (hot) conductor, to three lengths of black wire.
  2. Connect the first length of wire from the bundle, to a terminal on the single pole switch.
  3. Connect another length of wire from the bundle, to the common terminal on the double switch (the common terminal should be black, or some other odd color other than green).
  4. Connect the final length of wire from the bundle, to the brass colored LINE terminal on the GFCI.
  5. Connect the ungrounded (hot) conductor leading to the light, to the other terminal on the single pole switch.
  6. Connect the ungrounded (hot) conductors leading to the light/fan, to the terminals on the double switch.
  7. Connect the ungrounded (hot) conductor leading to the GFCI protected devices, to the brass colored LOAD terminal of the GFCI.
  8. Use a twist-on wire connector (or other approved means) to combine the incoming grounded (neutral), the grounded (neutral) from the light, the grounded (neutral) from the light/fan, and a length of white wire.
  9. Connect the length of wire from the neutral bundle, to the silver colored LINE terminal on the GFCI.
  10. Connect the grounded (neutral) conductor from the GFCI protected devices, to the silver LOAD terminal on the GFCI.
  11. Connect all grounding conductors in an approved manner.

NOTE: Notice that the grounded (neutral) conductor leading to the GFCI protected devices, is NOT connected to the other grounded (neutral) conductors in the box.

NOTE: Since I don't know the exact devices you're using, the terminal layout of the diagram might not be correct.