Long story short, I need to replace an electrical panel. In my the new panel the grounding bar is in a different location than the current panel. The ground wire from the Ufer rod will not reach to the new ground bar. Am I allowed to use a bonding terminal to "splice" a longer ground wire, or does it need to be one continuous wire?
Electrical – use a bonding terminal on ground wire between ufer rod and panel
electrical-panelgrounding
Related Topic
- Electrical – Can cold bond be connected to ground rod
- Adding second ground rod. Is this an acceptable way of bonding
- Electrical – adding a ground wire to a 2-wire breaker panel
- Electrical – Is it ok to use a ground rod at a subpanel instead of a fourth wire
- Electrical – Can the lug and breaker insert be rotated 180 degrees
- Electrical – Grounding in main panel without visible ground wire or ground bar
- Electrical – Sub panel neutral and ground not bonded so why continuity between them
- Electrical – use an existing Ground Rod for Sub-Panel in Detached Garage (Meter box is using the rod currently)
Best Answer
There's an easier fix for this
Get a Siemens EC1GB82 ground bar kit and mount it to the bottom-most set of ground bar holes in your loadcenter cabinet, with the large lug down. Then, you can simply terminate the annoyingly short ground wire to the bottom bar's large lug and call it a day.
This works because all the ground bars on a panel are electrically equivalent -- the cabinet connects them all together, by virtue of itself needing to be grounded.