I am retrofitting a Lutron Caseta dimmer switch to an existing light fixture in an older home. The fixture has line, neutral and ground, but the wire that was run to the switch box does not have a bare ground conductor. It does however possess a third, red wire that is unused on both ends. The Lutron Caseta needs to be grounded (since the fixture is Low Voltage). Can I connect the red wire to ground so the switch is grounded?
Electrical – use an unused red conductor as ground for a switch
electricalretrofit
Related Topic
- Electrical – safely disable a three way fan switch to use for providing ground to remote three way box
- Electrical – Replacing old switch with 2 red wires
- Electrical – Replace light switch connected to a power outlet with dimmer – two black wires to one black and red
- Electrical – Installing occupancy switch in a 2 gang scenario
- Electrical – How to connect the Lutron Casetas switch with only one hot (black) wire
- Electrical – Unused red for ground in existing armored cable
Best Answer
Not unless you wrap the entire length in green electrical tape, or you wired the circuit with 4 AWG or larger conductors. National Electrical Code says that equipment grounding conductors can be bare, covered, or insulated. It goes on to say "Individually covered or insulated equipment grounding conductors shall have a continuous outer finish that is either green or green with one or more yellow stripes..." (250.119).
If you wired the circuit with 4 AWG or larger conductors, then you can reidentify the red as ground. You just have to permanently identify the conductor at each end, and at every point where the conductor is accessible.