Electrical – use existing heater wiring to supply a sub-panel for two circuits

circuit breakerelectricalelectrical-panelwiring

I'm converting an existing sauna room to infrared. It currently has one 240/30A circuit. I have two heaters and one power supply/controller. Before purchasing I believed the power supply would handle powering both heaters from one on input side, but now I know two circuits are needed (PS has 4 inputs/4 outputs)

Each heater is 13A. Rather than run a 2nd circuit from the subpanel (would be difficult), I am hoping to add a small sub panel to split the 30A into two 15A circuits. The 30A is already coming from a subpanel but I wouldn't be making any changes there.

Is this approach ok or do I need to run a 2nd circuit?
power supply

Control panel

heatersoutlets for heaters

heater nameplate
Wire diagram back of door

So L1/N1 – L4/N4 on input side, L10/N10 – L40/N40 on output side
240v/30A coming in. I'm getting from this conversation that I'll need to replace the feed side 30A breaker with a 40A or 50A?

Best Answer

The posted pictures help a lot. Your heating elements are only 10.4 A each, so you don't need to change the breaker. The 13A in the part number is not the ampere rating.

You need to wire L1 and L2 together and N1 and N2 together in the control box. Each Ln is not indicating a phase but an input to the relays which are all isolated from each other so you have the option to run all the heaters on seperate breakers.

It looks like the equipment is only rated for 20A per circuit. This means that if you draw enough current through one heater to trip the breaker (say during a malfunction) then you may start the controller on fire before the breaker trips. In this case, I would recommend going with the subpanel and two 15 A two pole breakers feeding each of the two inputs you need to power. The only way it would work by pig-tailing is if all components are rated at the breaker capacity up to the point of additional circuit protection.