I am wiring three overhead florescent lights in my unfinished basement and I need 14/3 because of where the switch is located. The wiring already present between the fixtures is 14/2. I have a length of leftover 14/2 romex. Can I remove the sheathing and use each individual wire?

Best Answer

Short answer: NO

You may be able to use individual wires taken from a non-metallic cable (Romex is a brand) within a fixture, but not between fixtures or switches.

NEC 300.3(B) requires that:

All conductors of the same circuit ... shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord [with certain exceptions that do not apply here].