Electrical – Voltage between neutral and ground in receptacle

electrical

I have 10 outlets on the circuit. The first two check out fine. The rest show 120V between hot an d neutral and hot and ground. But they show 57V between neutral and ground. I unhooked the hot to a receptacle and still got 57V between neutral and ground? Any answers?

Best Answer

The 56V is just a nonsense figure you are getting because you have a high impedance voltmeter, and it doesn't know what to do with what it's seeing. This is the sign of a wire that is entirely disconnected from anything.

It's not attached at the panel side (because of a defect), and it's not attached to hot via any loads, because you have removed them.

If you plug in a load and turn it on, then the neutral should start behaving more predictably. This will also correct for the error produced by your meter.