The best I could do was to dig up a fine print note (FPN) in the National Electrical Code (NEC). In theory, there is no limit (as stated in other answers). In practice, the limit is when things stop working. In this FPN, the limit is 3-5%. In reality, the limit is around 1-2%.
NEC 2008
210.19 Conductors — Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
(1) General.
FPN No. 4: Conductors for branch circuits as defined in Article 100, sized to prevent a voltage drop exceeding 3 percent at the
farthest outlet of power, heating, and lighting loads, or combinations
of such loads, and where the maximum total voltage drop on both
feeders and branch circuits to the farthest outlet does not exceed 5
percent, provide reasonable efficiency of operation. See FPN No. 2 of
215.2(A)(3) for voltage drop on feeder conductors.
This Fine Print Note (FPN) says that to provide "reasonable efficiency of operation", the voltage drop of the branch circuit to the furthest point should not exceed 3%. And that the total voltage drop, including the feeders should not exceed 5%.
120V * 3% = 3.6V
120V * 5% = 6V
Given this information. You should start to examine your wiring, if you measure anything near 3V neutral to ground.
Note: Fine print notes are informational only and are not enforceable as requirements of the National Electrical Code.
Here is a highlighted image of a random electric dryer schematic.
Click for larger view
Notice that all the control circuits are 120V components, and that basically only the heater is 240V. Extending this image further, we can see how the dryer connects to a 120/240V split-phase system using a 3 wire cord.
Click for larger view
Due to the nature of the 120/240V split-phase system, the grounded (neutral) and grounding conductors in a dedicated single appliance circuit are basically the same. The dryer will work just fine whether the N
terminal is connected to a grounded (neutral) conductor, or a grounding conductor. However, connecting a NEMA 14-30R device in this way is nonstandard, and a code violation.
NEMA 14-30R
In the case of a three wire circuit, a NEMA 10-30R device should be installed.
NEMA 10-30R
When the wiring is connected to the proper device, the third wire in the cable becomes a grounded (neutral) conductor, and the code may be satisfied.
If you read point number three of the exception to section 250.140 of the National Electrical Code, you'll find that the neutral must be either insulated, or part of a Type SE cable. If this is not the case, your installation may still be a code violation.
An uninsulated, normally current carrying conductor running through your walls is typically a bad thing. Which is why this code exception is only valid, if the conductor is insulated.
tl;dr
Connecting a dryer in this way will work, but is a potentially dangerous code violation (according to the National Electrical Code).
If the receptacle is not of the self-contained variety, and is not in a box. That is defiantly a code violation (NEC 2011 406.5).
Extra Information:
If a proper 4 wire cable existed, the schematic from above would look something like this...
Click for larger view
If I've missed anything, or haven't explained something properly. Feel free to ask additional questions, or point out mistakes in the comments below.
Best Answer
The 56V is just a nonsense figure you are getting because you have a high impedance voltmeter, and it doesn't know what to do with what it's seeing. This is the sign of a wire that is entirely disconnected from anything.
It's not attached at the panel side (because of a defect), and it's not attached to hot via any loads, because you have removed them.
If you plug in a load and turn it on, then the neutral should start behaving more predictably. This will also correct for the error produced by your meter.