First of all, I wish all of you good strength and patience to overcome this bad situation with coronovirus
I am electrical engineer in the electricity company in Cyprus. I confess that I have no experience and knowledge in this matter.
I look forward to your kindness in answering my questions below:
Why do I measure voltages of the output terminals (secondary of isolating tranformer to earth ground? there is no connection to the earth…!! there is something missing….!! I did't understand…!!
I have an isolated transformer 2kVA 800V/230V. I am measuring as below:
-
between two terminals (not directly on the transformer output but on a MCB, 1m distance): 232V
-
between one terminal and earth: 175V
-
between the other terminal and earth: 49V
note: the primary of this transformer 800V/230V is the two Phases output (secondary) of a three phase transformer 22kV(Delta)/800V(Star).(the neutral – site of 800V – is grounded).
other question: If I have a small generator 230V without connection to earth will i measure voltage between the outputs terminals and earth ground? if yes … why..???
I need your help to undertand this measurments.
I will appreciate it
Thanks in advance
Best regards from Cyprus
Kyriacos
Best Answer
That there is no galvanic connection to earth does not mean there is no capacitative connection to earth. E.g. the transformer windings build a capacitance if the core is earthed. Wires could run close to grounded parts etc. This capacitative source impedance should be rather big, i.e. if a device of 20 or more Watt is connected to a phase and Earth, the voltage must drop.