Electrical – What range of heights are allowed for wall receptacles

electricalnecreceptacle

I need to mount a receptacle on a basement wall. If I can mount it high enough, it can go on the wood cripple wall instead of having to drill into the concrete and risk the excellent watertightness of the basement.

How high can the receptacle be placed and still count for the "within 6' of any point on the wall" requirement? While we're here, since it's related, what's the lowest allowable position?

Best Answer

The NEC doesn't count a receptacle above 5-1/2' to satisfy the requirement -

210.52(4) Located more than 1.7 m (51⁄2 ft) above the floor

The NEC doesn't have a lower limit for height, in fact 210.52(A)(3) allows floor receptacles within 18" of the wall to satisfy the requirement.

(3) Floor Receptacles. Receptacle outlets in floors shall not be counted as part of the required number of receptacle outlets unless located within 450 mm (18 in.) of the wall.

Now if there are any requirements for ADA accessibility, receptacles and switches must be between 15" and 48" and unobstructed.

ADA requirements