Electrical – What size and type wire should be used for 100 ft away work shop

electricalwiring

I built a shed a while back and. now I'm ready to get power to it.

I have a 50 amp GCFI breaker, that I plan to run the service line from to the shed. The shed is roughly 100ft away. I called a supplier and they recommended I go with 6 gauge copper or 4 gauge aluminum.

I'm curious which would be the better option?

To cavitate, I prefer the cheaper route as long as it is suitable for the application. The Aluminum 4 gauge is half the price of the 6 gauge copper, but both are reasonable.

Also, I plan on digging an 18-inch trench and running wire through PVC conduit.

Best Answer

Your voltage drop is almost the same for a 240v feeder at 100’ at a full load. 1.84% with copper and 1.91% for aluminum. I would save a few bucks and go with aluminum for a residential feeder, code had no hard standard for voltage drop but the recommendation is 3% at the sub and 5% an the end of the branch circuit. Remember you need 4 wire , 2 hot a ground and a neutral. Since it is detached you will also need a grounding electrode. If the 50 amp GFCI panel is in the shop ok but I would not recommend a GFCI feeder from your main panel, that’s a long way to walk for trips. Keep the GFCI protection local to the shed. The terminals on your panel and breakers are aluminum and copper compatible.