Electrical – What size and type wire should I use to pigtail to the light switches

electrical

  1. what's more common for light switches at home, 12 gauge or 14 gauge wire? how do I know what I have?
  2. I need to pigtail my ground and neutral wires to connect to my new leviton decora smart light switch. what do I ask at home depot to buy these pigtail ground and neutral wires?
  3. what does it mean by NM-B wire or THHN? I don't know which one to buy for my light switch, and don't know the exact specs to ask for. thanks

Best Answer

  1. Turn off the breaker for the device. Is it a 15-amp breaker? Use 14 gauge for pigtails. Is it a 20-amp breaker? Use 12 gauge for pigtails.

  2. Buy a few feet of the appropriate color of solid THHN and wirenuts. (THHN also comes in stranded, in this case you don’t want that.) As noted in a comment if you mean that you are going to use neutral as a bootleg ground, that’s a big no-no.

  3. NM-B, or Non-Metallic sheathed cable is a multi-conductor wire with at least hot/neutral/ground, commonly called Romex. THHN is a single conductor wire.