Electrical – What size breaker and wire do I need to run 2 GFCI receptacles and a flood light on exterior of the house

electricalwiring

Is it OK to use a 15amp breaker and a 14ga wire (14/2 copper) to run 2 GFCI receptacles and a flood light on the exterior of my home? The voltage is 120.

The 2 receptacles are rated at 15amps and won't be carrying a continuous load very often. Might plug a George foreman grill into it every now and then, maybe some party lights. And an occasional power tool (hedge trimmers, weed eater, etc.). I believe the flood lights are 75w a piece.

Should I go with a 20amp/12ga wire instead?

Update**

It is a new circuit so I think I will go with the 20A/12ga just to be safe and I will check the code requirements for having receptacles on the same circuits as lights!

Lets just it is OK to have both receptacles and lights on the same circuit. Is this an acceptable way to wire it? Using a junction box to divert wire towards the outlets and a separate wire to control the flood light with a switch on the same circuit? Pardon my drawing!

Circuit Diagram

Best Answer

There's no problem with anything you've suggested. You can use a 15 ampere breaker to protect 14 AWG copper conductors, without a problem. If you feel that 15 amperes is not enough for the receptacles, there is no problem installing 12 AWG wire with a 20 ampere breaker. It's completely up to you what you think is best. If the cost difference is not prohibitive, it may be worth installing #12 on a 20A breaker. Especially if you think you might plug in multiple higher load items at the same time (George Foreman and electric mower for example), or may consider adding additional receptacles in the future.

There is also no problem using a junction box to provide power to different devices. As long as the box is properly installed, accessible, sized appropriately, and adequately sealed.

Nothing in electrical code says that lights and receptacles cannot be on the same circuit. It's more of a guideline than a rule. The general idea is that if the vacuum trips the breaker, you don't want to be left standing in the dark.

The only problem I see, is with the GFCI receptacles in your drawing. You will not need two GFCI receptacles. You'll simply feed the second receptacle, from the load side of the GFCI receptacle. When wired this way, the GFCI receptacle provides protection to the downstream receptacle.