Electrical – What size equipment grounding conductor is needed for this gate lights circuit

electricalgrounding-and-bonding

We live in a rural area and I am running a circuit to to our gate for a couple of post lights and maybe a receptacle. The run is 485 feet from the closest panel. I am installing THHN wire in a 1" diameter PVC conduit. Due to the low amperage draw of the lights (<5 amps) I can calculated I can get by with #6 THHN. I will install a 15 amp breaker on this dedicated circuit. My question is can I get by with a #8 ground or should I run a #6 THHN ground as well?

Best Answer

Where the grounding conductors are increased in size (from the minimum) the grounding conductor also needs to be increased in size proportionately per 2014 NEC 250.122. I used the southwire voltage drop calculator. The calculated value needed for a 5 amp draw is #8 copper for 5 amp load at this distance 2.8% voltage drop. The problem with down sizing the conductor in this case would come if the lighting was changed at a later date using more of the available ampacity of the circuit then the conductor would be under sized. 120V @ 12 amps would require a #4 conductor and the #8 would be two small to limit the voltage drop for a short circuit.