Electrical – What size grounding wire for a main lug

electrical-panelgrounding

I am replacing an undersized 35 amp main lug, so the panel, conductors and breaker in the main panel are all being replaced.

The new panel will be 125 amp rated, the new conductors will be #3 THHN, with an ampacity rating of 115, which will be protected by a 100 amp 2 pole breaker in the main panel.

What size does the grounding conductor leading back to the main panel need to be?

This calculator seems to indicate I need a #8 copper conductor, but I'm not sure this is the correct table for me to use.

This project must be done to code for Arapahoe county Colorado (2017 NEC)

Best Answer

It actually depends on whether the ground is going to be installed ahead of the main breaker or if it is installed after the main. Most of the contractors I know will install a #6 simply because it is less expensive to stock one size than two and it covers everything up to a 200A main. So I would go with a #6. 2014 NEC reference Tables 250.102(C)(1) and Table 250.122.

Use extreme caution when working around panelboards. I recommend DIYers make sure the panel is disconnected from all power sources before performing any work.

Hope this helps.