I need to run power from my house out to my 35X70 workshop out back. What I have; a dedicated panel with 150 amp breaker on the side of my house that is currently only powering my well. My workshop is 275 ft. away. I intend on putting a 100 amp sub-panel in the shop. I have most of the 2” conduit ran in a trench from my house to the workshop. I intend on having a welder, compressor, wall unit a/c in a small office, lights and maybe an outside outlet to hook up for a travel trailer. I want to use copper wiring. What main wiring is recommended to run inside the conduit from the 150 amp/panel on the house to the 100 amp sub-panel in the workshop?

Best Answer

I use Southwire's wire size calculator.

At that length aluminum feeder would be much cheaper, selective boxes for; feet, single (phase), aluminum, direct burial/conduit/overhead, minimum conductor size, input 275 (for the length), input 240v for the voltage, max voltage drop leave at 3 (but we will play with this), current at end (since you don’t know guess at 80), input 1 for parallel sets.

This came up for 2/0 with a standard 3%. Input in 5 in the % and the wire size drops to 1 awg with a 4.44% voltage drop

In the US the National Electric Code there are suggestions of 3% and 5% for voltage drop but these are only suggestions.

If you actually used 80 amps of 240v then the drop would be 10.6v with 1awg or #1 wire not a problem.

if you are drawing 50 amps 240v on the #1 wire the voltage drop would be only 6.6volts (got that by playing with the amperage and % voltage drop).

Only during really heavy loading of your circuit would #1 aluminum have a voltage drop that was at the max recommended by the NEC and it never exceeds 5% up to 80 amps.

Going to a larger feeder breaker 90 or 100 requires a larger wire size but I doubt you will need that much power.

I would get the 150 amp panel with more circuits you can feed it with anything below 150 as long as the wire size matches the feeder wire requirements.