I am planning to run power to a very small shed by extending an existing 15a circuit that currently feed only a gate operator (4.5amp). This is located in southeast Michigan. I only need power at the shed for a light and a single receptacle for the occasional small power tool. The gate is fed by (3) #14 wire in PVC conduit about 100'. I plan to tap into the existing junction box at the gate and run THWN #14 wire underground (18" depth) in a 3/4" conduit about 75' to the shed. I will use a small disconnect and a GFCI at the first receptacle. My questions:

  1. Will there be a problem with voltage drop if running #14 wire that far? I assume it does no good to run heavier wire unless I replace the existing run of #14 with the same.
  2. Is schedule 40 PVC conduit sufficient for running a 120v, 15amp circuit 18" down in a residential yard?

Best Answer

#14 is not adequate for a 175 foot, 50% circuit capacity load. Voltage drop is a function of resistance of the wire in series with the load. Extending a #14 circuit with lower resistance #12 is completely acceptable and does accomplish reducing the accumulated resistance that causes voltage loss on the extension.

5% is the total drop generally considered the maximum acceptable. Figure a distance to the gate of 100', add your 75' extension, you have 175', with an 7.5 amp load (a worm drive saw) you have a 3.5% loss just getting to the gate, then an additional 3% getting to your new receptacle. But if you reduce the resistance on the extension by using #12 you will get only about 1.5% loss on your extension, bringing you back to 5%. (Numbers get dramatically worse if you exceed the 50% circuit capacity that I used above.)

The 18" cover requirement is adequate for most conditions, be aware it is 18" of "cover", meaning the conduit is to be below 18" of material. Do an internet search for table 300.5 that could identify conditions that could change depth requirements.