I need to install a sub-panel in a shed. Total run distance from main panel to sub-panel is 80 ft and includes three 90 degree turns. Burial distance will be 18". I'm thinking to install a 60-amp main breaker in the sub-panel and running #6-3 THWN in 1-1/4" PVC conduit. I hesitate using direct buried cable as it seems a bit more vulnerable (but I'm no expert). I will be driving an 8' ground rod. A worst case inventory of expected loads is about 30-amps (1500 watt heater, 300 watts in lighting, 12.5-amp table saw, other?). This gives me a bit of room to grow. Am I doing anything stupid?
Electrical – What wire type & size for sub-panel in a shed
electricalsubpanelwiring
Related Topic
- Electrical – Big Problem: buried feed to outbuilding sub-panel. Not really buried
- Electrical – Long outside wire run – can I JUST ground at both ends
- Wiring – How to wire a sub panel from a 15 amp circuit existing run
- Electrical – Wiring Pool Subpanel for Pump and Receptacles
- Wire a sub-panel to run a pottery kiln, or put a breaker in the main panel
- Electrical – What wire do I need
- Electrical – Is a 200 amp service adequate for two RVs
- Electrical – Do i need a subpanel for a single circuit with less than 4 receptacles equaling less than 600 watt load. Washington state
Best Answer
Well, I would not say you're doing anything stupid. You have some very good questions.
First,
Second, Consider voltage drop:
That is less than 3% which the NEC recommends for a feeder. Very Good !
Note: I would hesitate to install the ground rod if you have a in-ground pool in line of the transformer.Correction: This being a feeder would require a grounding electrode!