Electrical – What wire type & size for sub-panel in a shed

electricalsubpanelwiring

I need to install a sub-panel in a shed. Total run distance from main panel to sub-panel is 80 ft and includes three 90 degree turns. Burial distance will be 18". I'm thinking to install a 60-amp main breaker in the sub-panel and running #6-3 THWN in 1-1/4" PVC conduit. I hesitate using direct buried cable as it seems a bit more vulnerable (but I'm no expert). I will be driving an 8' ground rod. A worst case inventory of expected loads is about 30-amps (1500 watt heater, 300 watts in lighting, 12.5-amp table saw, other?). This gives me a bit of room to grow. Am I doing anything stupid?

Best Answer

Well, I would not say you're doing anything stupid. You have some very good questions.

First,

  • If you did decide to direct bury the wire the minimum depth for direct burial is 24", not 18".
  • At least three #6 ( black, red, white) and one #10 insulated ground ( green coating).
  • Anything <= 60amps just requires a #10 insulated ground with green coating.

Second, Consider voltage drop:

  • Load: 30 Amps @ 240V Single Phase.
  • Length of run: 80 feet
  • Wire Size: #6 Copper
  • Voltage: 240V
  • Voltage Drop: .81 %
  • Voltage At End of Circuit: 238.05

That is less than 3% which the NEC recommends for a feeder. Very Good !

Note: I would hesitate to install the ground rod if you have a in-ground pool in line of the transformer.

Correction: This being a feeder would require a grounding electrode!