First, your illustrations are Mad Awesome. You could illustrate electrical books. Literally. You might even talk to Mike Holt or others doing electrical docs.
You still have some knowledge gaps, so I'd school up some more. For a guy as smart as you, knowledge is cheap.
If you are good at visual, stay with that. Buy a variety-pack of electrical tape colors, and a couple feet of 12/3 cable because it's a cheap way to get a variety of wire colors for pigtails. 12 gauge is the universal donor size, it is acceptable on any common 120v circuit up to 20 amp breaker. 14ga is only allowed on 15A breakers/with 14ga wire.
![NM Romex cables](https://i.stack.imgur.com/kgXxJ.jpg)
First, permanently wrap (tag) the white wire of cable C with red tape. From your comments elsewhere that there is only one cable going to the switch, that is a switch loop. Also open up the switch box and wrap the other end of that same white wire.
Next, permanently wrap (tag) the black wire of cable A with red tape. Since the switch is a switch loop, this cable is the only possible way the lights could possibly be receiving (switched) power.
Now grab your receptacle and some stripped Romex and sit at a convenient workbench. Put 6" pigtails of wire as follows. Use the screw terminals or screw-and-clamp if you have that type. Avoid backstabs (they're not reliable) and never use 12AWG on a backstab.
- Ground terminal: a bare (or green) wire.
- screw 1: a white wire.
- screw 2: nothing, but if the tab between 1 and 2 has been broken, a white wire.
- screw 3: a black wire.
- screw 4: nothing, but if the tab between 3 and 4 is broken, a black wire.
Ready?
Splice all same colors together.
See, what I did was color-code all the wires to their function rather than the default colors of /2 cable. The switch loop has only hot (black) and switched-hot (red). The wire to the lights needs switched-hot (red) and real neutral (white).
In new work, they commonly use red for the switched hot, because the law now requires neutral in switch loops (for smart switches). So they run some /3 cable up there.
Best Answer
In a residential load calculation, general-use receptacles are included in with the 3 volt-ampere (VA) per square foot general lighting value.
In other than dwelling units, receptacles are calculated at 180 VA.
If you wanted to use the 180 VA value, it would be 1.5 amperes (
180VA / 120V = 1.5 A
).