Simply replacing the first receptacle in the group with a GFCI receptacle, will provide protection to the entire group (if wired properly).
GFCI Receptacle
Locate the feeders
WARNING:
This procedure should only be carried out by persons with the proper tools and knowledge. And should be carried out with extreme caution.
When you open up the box containing the first receptacle in the group, you're going to notice two cables enter the box. One cable brings power from the breaker/fuse box (feeder), and the other carries power to the remainder of the circuit. You'll have to figure out which cable is which, so you know how to connect the GFCI receptacle.
- Start by turning off the power at the breaker/fuse box.
- Disconnect the receptacle, and position all the wires so that they will not contact each other or anything else conductive.
- Turn the power back on.
- Using a multi-, voltage or non-contact meter determine which set of wires is which. The feed from the breaker/fuse box will have power, while the line going to the rest of the circuit will not.
- Mark the wires in some way, and turn the power back off.
WARNING:
If you got a voltage reading on more than one set of wires, STOP, do not follow the rest of these instructions. contact a local Electrician.
Connect the GFCI
On the GFCI receptacle you'll notice that one set of terminals is labeled "LINE", and the other is labeled "LOAD".
- Connect the wires from the cable you marked as being from the breaker/fuse box, to the terminals labeled "LINE" (Black to brass, white to silver, green/bare to green/ground and the box if it's metal).
- Connect the wires from the other cable to the terminals labeled "LOAD".
- Install the receptacle into the box.
- Turn the power on.
- Press the Reset button on the GFCI receptacle.
WARNING:
If the receptacle will not reset, the wiring is connected incorrectly, or contains a fault. Contact an Electrician to complete the job.
GFCI Breaker
Alternatively, you can install a GFCI breaker to protect the entire circuit.
WARNING:
This procedure should only be carried out by persons with the proper tools and knowledge. And should be carried out with extreme caution.
- Turn off the breaker.
- Remove the black wire from the terminal on the breaker.
- Locate the white "neutral" wire associated with the circuit (should originate from the same cable).
- Remove the white "neutral" wire from the neutral bus bar.
- Remove the breaker (Caution should be used not to touch the hot bus bar while the breaker is removed).
- Install the GFCI breaker.
- Connect the white wire from the GFCI breaker to the neutral bus bar.
- Connect the white "neutral" wire from the circuit to the GFCI breaker.
- Connect the black "hot" wire from the circuit to the GFCI breaker.
- Turn the breaker on.
WARNING:
If the breaker will not reset, the wiring is connected incorrectly, or contains a fault. Contact an Electrician to complete the job.
Test the GFCI
Once the GFCI device is installed, it should be tested at least once a month to insure it's functioning properly.
- Press the Test button.
- Press the Reset button.
If the GFCI will not reset, the GFCI is bad, the wiring is incorrect, or there is a fault. Correct any faults, and/or install a new GFCI device.
First off. The only way to provide proper "grounding", is to install a grounding conductor from the panel to each outlet. Providing AFCI and GFCI protection to the circuits is helpful, but these devices will not provide "grounding".
If you switch from 2-prong receptacles to 3-prong on these circuits, you should not connect anything to the grounding screw of the receptacles. You should also (technically) install labels at each outlet that read "GFCI protection" and "No Equipment Ground". Though, these labels aren't common in residential situations.
- Replace GFCI breakers with CAFCI breakers and add GFCI receptacles to the first-outlet on each circuit.
This is probably going to be your best bet. In this scenario, the CAFCI breaker provides protection to the entire circuit. The GFCI protection being at the first outlet, means that while the wiring from the panel to this location is not protected, the rest of the circuit is protected.
- Keep GFCI breakers and add AFCI receptacles to the first-outlet on each circuit.
This isn't a terrible option, although the AFCI device will not be protecting the wiring between the panel and the device. Also note that an AFCI device only detects line to ground arcs (parallel arcs), while a CAFCI device detects both line to ground and line to line arcs (parallel and series arcs).
- Replace GFCI breakers with Dual Function AFCI/GFCI breakers.
If you could actually find these (and could afford them), this would probably be your best course of action. Unfortunately, these devices probably don't exists (yet) from most manufacturers.
Best Answer
The NEC simply states "where supplied through a ground-fault circuit interrupter" in this instance, so you can achieve this either by a GFI receptacle, a faceless GFI device, or a GFI breaker.
You cannot however use an AFCI breaker, unless it is one of the new (and rare) AFCI/GFCI breakers. Good luck finding one though. I find one Siemens on Amazon and that's about it.
See "(c)" below.
From the 2011 NEC: