I have a Weil-McLain HE2 series 1 boiler and am attempting to attach a Honeywell RTH6500 wifi thermostat to the main floor. The house has 4 zones and therefor 4 separate thermostats. The main floor thermostat has an extra (green wire) in addition to a red and white at the thermostat. There is only heat, no AC, fueled by propane. I attached the thermostat on the main floor and with the Cwire attached to the neutral side of the external transformer, the thermostat powers up, but cycles off and on when calling for heat. There is an additional transformer inside the boiler unit with a pink and brown wire. Where should I attach the C wire at the boiler?
Electrical – Where to connect thermostat C wire to Weil-McLain HE2 series 1 boiler
electrical
Related Topic
- Electrical – How to install a WiFi thermostat with a Well-McLain steam boiler
- Electrical – Where should I connect the C wire in a Janitrol furnace
- Electrical – use a WiFi thermostat without a C wire
- Electrical – Honeywell zone panel turning on cool of instead of heat
- Electrical – Where is the C wire terminal on the boiler
Best Answer
Both this document (PDF) and this document (PDF), say that one 24V-40VA transformer can only support 3 zone valves. Since you have 4 valves, you're over the recommended number of valves. Once you added the demand of the WiFi thermostat, you likely overwhelmed the transformer. The answer here, may be to install an additional transformer.
There's a diagram in the second document, that shows how to wire in an additional transformer. This document also has a good explanation of how the valve actually works, which might be worth a read.
Based on these documents, a WiFi thermostat should be wired in like this.
Based on the your description of the wiring, it sounds like it's a bit different than that of the documentation. Incorrectly wired valves might also be the problem. Based on the documentation, terminals
1
and2
are connected through a heater, while terminals2
and3
are connected only when the valve is open.When the thermostat closes (calls for heat), current flows from terminal
1
, through the heater, to terminal2
. Once the valve opens, a contact allows current to flow between terminals2
and3
. So basically energizing1
and2
opens the valve, and energizing2
and3
signals the boiler to circulate.