I setup a kiln at our building, and I realized that the electrical system is setup with a three-wire feed – two hots and a neutral. This is fed from a three phase system, though, so the voltage over the two hots is 208v instead of 240v.
Why would something be setup in this way? Doesn't three phase wiring require all phases to be used in order for it to be balanced?
Best Answer
Phase balance is handled upstream from the meter socket
You will see this in two places:
Either way, what will happen is that the buildings or tenant spaces will be connected to 2 of the 3 phases to get a 3-wire service from the 4-wire wye system, but the phases they get will be rotated/transposed to balance the load:
This way, you get an evenly balanced load from several 3-wire services on a 4-wire system. Furthermore, a similar pattern occurs if you go down a 3-phase panel on a 208Y/120 system plugging 2-pole breakers into one side of the panel:
As to implementing this: