Electrical Panel – Why Are There Two Grounding Bars in the Breaker Box?

electrical-panel

I just purchased a trailer that was used for dog grooming. It is fully wired with for 120 volts AC. All the wires in the breaker box have been disconnected. I have already toned the wires to identify their use. I am going to hook the trailer up to the on board Generator that came with it. I will not be using shore power only the Generator power. When I looked into the breaker box and it has 2 grounding blocks. The block on the left is grounded to the box, the block on the right is not grounded to the box. I am wondering what the block on the right would be for? I am building a food trailer so i want to make sure that everything is grounded properly. Would i connect both the ground and the white to the block on the left? Also the Generator is only a 120 volt AC output. Thank you for your help with this matter.enter image description hereenter image description here

Best Answer

The isolated bar is intended for Neutral.

If, like many generators, yours has ground and neutral bonded inside the generator, your generator neutral and all neutral wires go to the isolated bar, and the ground wires go to the one connected to the box.

That also sets you up properly for a "shore power" input.

Your hot feed either goes to one of the line inputs and you only use that half of the breaker spaces, or you connect your hot feed to both line inputs with a jumper, since this is 120V only, so there won't be any 240V dual-breakers. The former leaves the ability to connect to shore power (or a larger generator) "properly" and the latter does not (but will work if you are only plugging into a 120V-only shore connection.)