Electrical – Why does the GFCI trip when I plug things into load side receptacles

electricalgfci

I installed a new outdoor circuit. The line comes out of the house and into the LINE side of the GFCI outlet. I connected a wire to the LOAD side and ran it to two standard outlets downstream. My tester says the circuit is wired properly at all the outlets; the tester button appropriately trips the GFCI when used.

Here's the problem: devices plugged directly into the GFCI outlet work fine. However, when I plug the same devices (I tested a light, a fan, and a grounded shop vac) into the downstream outlets, they trip the GFCI.

I'm stumped. Help?

Best Answer

Check for a neutral to ground short somewhere on the load side of the GFCI and downstream outlets. Also, make sure there isn't a shared neutral with any other circuit and that you don't have a connection from the neutral load directly to the line side of the GFCI (in other words, the whites cannot all be pigtailed together, the line and load neutrals must be separated by the GFCI).