Electrical – Why don’t conduit fill rules apply to cables encased in closed-cell foam

electricalinsulationspray-foamwiring

I have a question that is more theoretical in nature. I know that when you have 14/2 cable and put it in a 1/2 conduit you are above fill (or just at max fill). The NEC cites that this is in part due to heat dissipation.

300.17 Number and Size of Conductors in Raceway. The number and size of conductors in any raceway shall not be more than will permit
dissipation of the heat and ready installation or withdrawal of the
conductors without damage to the conductors or to their insulation.

Consider a close-celled foam installation:

The cables are usually entirely encased in the stud-bays (even less clearance than in 1/2 conduit), and while foam is a good insulator it is a bad heat-sink; it doesn't allow good heat-dissipation due to there being little to no air.

Since I've seen a few foam installations where the cable is completely covered there must not be a code regarding it, and I was just wondering why? Doesn't the foam pose an issue for heat dissipation?

Please when answering cite official sources if at all possible and don't rely on conjecture.

enter image description here

Additional section of interest:

310.15.3

(3) The rate at which generated heat dissipates into the ambient
medium. Thermal insulation that covers or surrounds conductors affects
the rate of heat dissipation. (4) Adjacent load-carrying conductors —
adjacent conductors have the dual effect of raising the ambient
temperature and impeding heat dissipation.

Best Answer

The foam isn't the issue, but a lack of spacing can be

Foaming NM cables into a wall (or otherwise burying them in thermal insulation) isn't considered to be an issue, provided that the cables were originally run in a manner that maintains proper spacing between them. However, not all installers are that careful, and for those who aren't, they find themselves staring at the third paragraph of NEC 334.80:

Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(3)(a).

This covers the issues with mutual heating that you allude to when the current-carrying conductors are actually adjacent to each other, such as when a bunch of NM cables are run together. However, with the cables spaced out properly, they will sit separated by thermal insulation, which prevents the cables from heating each other up.