I am in the throes of learning enough to do a DIY install of a small heat pump package unit.
The installation manual calls for (and suggests that NEC requires) a "fused disconnect" inline with the power from the panel to the main unit.
I have two points of confusion on this. If my HVAC unit is right next to the main breaker box (like 3 feet away), what's the point of this (to my mind) "extra" disconnect box?
- why does it need a "fuse" (the breaker will be dedicated to the hvac unit)
- why does the HVAC needs its own dedicated disconnect rather than just shutting off the aforementioned breaker in the breaker box (right next to the HVAC unit)?
While we're at it, this is 2015… does ANYTHING in residential wiring still use an actual "fuse"? Why would it be a fuse rather than a breaker?
Best Answer
Disconnects are required when the equipment is too far from, or not within sight of the breaker (or branch circuit disconnect) (commonly known as "Serviceman disconnects" or "Serviceman switches"). This is required so that while you're working on the equipment, it's less likely somebody will accidentally energize the equipment (flip the breaker on).
Fuses are used for overload protection, mostly for motors. The fuse is typically sized to the motor load it's protecting, and may or may not be a different size than the circuit breaker. If a motor can't spin, it will quickly overload, overheat, and burn up. A fuse is used to prevent that.
For more information on protecting the equipment, and sizing the protection. See the rest of article 440. As Mjohns answer points out, the manufacturer's documentation rules, so make sure you read and understand it.