I have 4 GE AFCIs in a GE subpanel in my basement. Occasionally, when I turn on a bank of dimmable CFL lights via a CFL-rated dimmer switch, I get a trip in a particular AFCI breaker that's on the other phase. This doesn't happen every time, and it seems to happen more when the dimmer isn't set to full brightness. Resetting the breaker gets the power back on with no issues, but I'm tired of this.

I'm at a loss as to why a different circuit on a different phase is tripping, and even more confused why it happens only some of the time. These are not MWBCs, but obviously share the neutral in the panel feeder. Nothing else causes any other trips anywhere else in the house that aren't obvious, like 4 hair driers on a 15A circuit.

What's going on here? How can I find the cause of this?

Best Answer

The dimmers are spewing radio-frequency hash into the power line, which confuses the AFCI into a false trip. It makes sense that it's more reproducible on an intermediate dimmer setting, because that's when the dimmer chops the line voltage aggressively, not when it's fully on or fully off.

Bypass capacitors could help with this: 1 to 10 nF capacitors, X1/Y2 rated ceramic or film, minimum 250VAC working voltage rating. This diagrams shows three caps: between hot and neutral, hot and ground, and between neutral and ground.

The basic idea is that 60 Hz AC will not pass through these capacitors because the frequency is too low, but radio frequencies pass through easily. So the capacitors provide a short circuit shunt path for high frequencies, reducing how much of it spews back upstream from the dimmer.

enter image description here

This looks simple, and it is, but it has to be done properly. Capacitors have long, uninsulated terminals, creating opportunities for short circuits if you're not careful.

Instead of these ad-hoc capacitors, you can install an EMI filter upstream from the light dimmer. EMI filters have a more sophisticated circuit which includes inductors.

One more thing: the Lutron dimmer company sells a filtering component that they call a lamp debuzzing coil.