I'm having trouble installing a WEMO wall switch. The light I want to use it on is a single on/off switch, not a 3 way switch. When I remove the face plate, the neutral wire is wired to the light switch on its own. It's not connected to the other neutral wires that fit in the multiple light switch housing. I have tried connecting but it does not function. What does it mean when the neutral wire is connected to the light switch itself and not bundled with the other neutral wires?
Electrical – Why would a light switch be wired with the neutral wire
electricallightingswitchwiring
Related Solutions
SHORT ANSWER
You can't convert the WeMo switch to replace a three way. You can add it to a three way circuit to turn lights on and off if and only if the three ways were first set to leave the light on. When you turn off the WeMo (at home or remotely), the lights will go off. When you turn on the WeMo (at home or remotely) the lights will go on. But, if the lights are already off because the three ways were used to turn them off, the WeMo will not turn them on.
LONG STORY
The WeMo light switch is a simple on and off switch (as far as your electrical system is concerned; yes, I know it does more). It allows a circuit to be on or off, based on whether that switch is on or off, period.
A three way switch also turns a circuit on or off. The difference is a three way switch is one of a pair. Each switch changes the state that the other switch has created. For the switch closest to the power supply (A), current comes into the switch on one side (on the common terminal) and leaves the switch on one of the two terminals on the other side (the travelers), depending on which direction the switch is thrown.
On the second three way switch (B), closer to the light or other device, the power comes in on one of the two travelers and leaves the switch via the common if and only if the switch is thrown to the same traveler as switch A.
For three way switches, there is no on or off position. Rather there is traveler 1 and traveler 2 positions (not labeled that way but called that for illustration). The circuit is on when both switches are turned to the same traveler and off when they are turned to different travelers.
This illustration also shows the 4-way switch described by OP.
It also does NOT show neutral and ground wires which MUST be connected as well.
All of the illustrations show just one ON position for the 3-way/4-way setup.
There are actually four possible ON combinations and four OFF combination.
The WeMo can be added to this circuit by placing it between the hot line and the common terminal on three way switch A or between the common terminal and the fixture on switch B.
or
These illustrations do NOT show neutral and ground wires which MUST be connected as well.
WeMo effectively interrupts or connects the power either before or after it goes through the three way setup. However, If it three way pair is off (the swithces are not turned to the same traveler), then the circuit will stay of, regardless of the WeMo setting.
Whether this works for you depends on whether you are willing to be sure to turn the three way setup to on before you leave and then control the system with the WeMo.
THE SETUP
The existing switch you are describing does not sound like a three way, but a four way. This is a switch used between two three ways to give an additional location to switch a circuit on and off. (The white wires are actually being used as hot lines and should have been marked with black tape or a black marker). This switch cannot be controlled by the WeMo. You need to find the one of the real three ways to make this work.
When you do, connect the wires as follows:
- WeMo GREEN wire to the BARE wires in the box.
- WeMo WHITE to WHITE wires in the box.
If you are placing the WeMo next to three way A (closer to line voltage):
- WeMo BLACK (Lightning bolt) to BLACK or RED power line currently attached to COMMON terminal on existing three way switch.
- WeMo BLACK (Light bulb) to COMMON terminal of existing three way switch.
If you are placing the WeMo next to three way B (closer to fixture):
- WeMo BLACK (Lightning bolt) to COMMON terminal of existing three way switch.
- WeMo BLACK (Light bulb) to BLACK or RED power line currently attached to COMMON terminal on existing three way switch.
REMEMBER, the three way setup has to be set so that the circuit is ON for the WeMo to be able to control it remotely. (The four way you have been looking at complicates the circuitry, but you can effectively ignore it; just make sure the overall circuit is ON before you leave; it doesn't matter which switch you flip to turn it on.)
SUPPLEMENT
Based on the OP's comment, he or she is willing to lose the 3/4-way functionality and install the WeMo only to control the fixture. That cannot be done by replacing the 4-way switch described because there is no neutral in that box.
The WeMo could be swapped for one of the three ways if there is a neutral in the three way box.
If you are replacing 3-way A, attach the black lightning wire to the black (or red) hot from the line. Attach the black lamp wire from the switch to the black traveler. Cap the white traveler. In the 4-way box, remove the switch and join the two black traveler wires. Cap the whites separately. Place a blank cover plate over the box. In switch box B (closest to fixture) remove the switch. Attach the black traveler wire to the fixture wire. Cap the white traveler wire.
If you are replacing 3-way B, follow the same steps, except in box A, the black traveler is attached to the hot line, and in Box B the black lightning wire is attached to the black traveler and the black lamp wire is attached to the fixture wire.
You have some pretty weird wiring to the light fitting. It looks like at the light fitting (fed from top-right romex at box) you would find
- the "ground" wire (green or bare copper in the US?) is being used as a neutral return from the light bulb.
- the "hot" (black) is a switched hot to the light bulb.
- the "neutral wire (white) is being used as a permanent hot for some other purpose.
So I'd expect an ordinary light fitting to be using the false "ground" and switched hot wires only.
The permanent hot (false neutral, white) might have been used (now or previously) to power some kind of device that needs live power. For example a remote light control or a ceiling fan that is operated by a pull-cord independently of the light bulb itself.
I would check the wiring in the light fitting controlled by that switch. Then I'd label the wires at each end to make clear what each wire is really used for. Alternatively, you could rewire it properly - that would be best if the light fitting is a normal conventional simple light only. I'd double check that something else (an extra outlet?) isn't already wired from the light fitting end - disconnect the white wire from the three black and see if an outlet or something stops working.
If you can't figure it out it might be best to call an electrician.
Related Topic
- Electrical – Trying to Replace 3-Way Light Switch
- Electrical – Replacing light switch with dimmer switch… white wire
- Electrical – Any issue connecting neutral and ground of bluetooth light switch to ground (or neutral)
- Wiring – Why is the light switch wired this way
- Electrical – Why would a switch be wired with its neutral connected to ground
- Switch – Trying to identify neutral wire in switch box to use with Wemo Light switch (more than one neutral wire seems to be present)
- Electrical – connect a shared neutral to the Wemo smart light switch
- Wiring – Ceiling fan with light – electrical box has two cables, one with a red wire
Best Answer
If all you have is one wire entering the switch, then the power for the switch might come from the light, and you just have a switched hot.
The white wire should be marked with tape to indicate it's not being used as a neutral.
Unfortunately, if this is the case, then you don't have a neutral available at this switch which is necessary for most of these automation switches. If there are other switches in this box it might be possible to re-route the power for this light, but I'd need to know more about where the power is coming from, what else is there, and how the light is connected in the ceiling box to help. Otherwise, the only way to this would be to run a new wire to the switch location -- either a new 14/3 from the light (so you have hot, neutral and switched hot), or a new power feed with 14/2 from the panel.