How many cables are you allowed to run through a single hole in a wooden floor joist?
We have a question and good answers for the NEC guidelines. Why would an inspection company flag this and note that there is an "overheating" chance?
Note that these wires are on the same circuit and oversized (just going to canned lights).
Is there any new guidelines I am missing here?
Best Answer
What they're probably trying to flag...
The usual thing that gets cited for this is the second paragraph of NEC 334.80 (text from 2017, but this hasn't changed much -- 320.80 is a newer extension of it that applies to AC/BX):
...and why their cite's a swing and a miss
However, even though the 24" exception (which is the exception cited in the quote above) is ruled out in this case, because ampacity adjustments on NM cables are permitted to be made from the 90°C column ampacity in the table by the first paragraph of that very same section:
As a result of that fact, we can start with the 25A 90°C ampacity of 14AWG copper (or the 30A figure for 12AWG copper), and then start adjusting it accordingly, based on the number of cables (really, current-carrying conductors) we have present:
So, unless you're cramming 5 cables (whether /2 or /3, in most cases) into a single hole, or using archaic cables that lack 90°C rated insulation (all modern NM is NM-B, which means that the wire insulation is 90°C rated), then you're good to go.