Electrical – Will a 15A receptacle on a 20A circuit fail if I draw over 15A combined from each outlet

electrical

OR: is the rating for the entire receptacle or each outlet individually?

A common 15A receptacle has two outlets. If such a receptacle is attached to a 20A circuit, an 8A draw from each outlet will not trip the breaker.

Should such a draw cause the receptacle to fail? Or is the rating for each outlet contained in the receptacle?

Best Answer

No.

For a receptacle to be rated for 15A, it must be able to handle 15A at either outlet. For example. If you plug one item that draws 15A into a receptacle, the receptacle must be able to handle that current.

Receptacles are actually designed to handle 150% over their rated current (or something like that, I'd have to find the specification to be sure). A 15A receptacle should be able to handle 22.5A, so your breaker should trip before the receptacle fails.

Consider this image...

enter image description here

Assuming the tab between the hot terminals is removed, and the red and black wires are each connected to separate 15A breakers. This is a valid configuration, and would allow 15A to be drawn at each outlet.

However, It's usually not a good idea to tempt fate, or stress test electrical components. So in theory, it will not fail. In practice, it should not fail.