Electrical – Will These Electrical Panels Support Hot Tub

electricalelectrical-panelhot-tub

I’m trying to have a hot tub installed that requires a 50amp breaker.

My main panel is a quad-throw 200amp service see photo #1 This main panel feeds 2 other sub panels – one to the garage and one to the basement. I’m wanting to have the hot tub 50amp breaker installed from the garage sub pane – picture #2. I’m worried that since the main panel appears to be feeding 125amps mac to the garage panel and 50amps of that is going to be used by the hot tub that there won’t be enough amps left in that sub panel (125 total) and things will start tripping.

Am I over concerned?

enter image description here

enter image description here

Best Answer

I assume the 2nd pic is the sub-panel in your garage? If so, you should be fine installing the breaker for the hot-tub in the garage, since it has a 125 amp feed. That is unless you have lots of other simultaneous heavy loads, which I don't see breakers for. Just because the amperage of the breakers adds up 170 amps in that panel isn't a problem. Panels are over-subscribed all the time.

Using the capacity of every breaker at the same time, is a virtual impossibility.

The heating element size in common hot-tubs is 4 - 5.5 KW which is 16.6 amps and 23 amps respectively. And it will not nearly be on all the time. Additional draws will come when you use it and start running pumps. But the total draw will be less than 50 amps.

Again, just because you have the circuit capacity doesn't mean you are using it. If you were using all the capacity of every circuit in your house (ignoring the fact the main breaker would trip), you'd need a very large loan to pay your electric bill!