Electrical – Wire size. 125 feet underground to 100 amp sub panel

electrical

I have an outbuilding will be 125 feet from panel to panel. Sub panel in put building will be 100 amp. Main panel at 200 amp. Want to have a direct burial line 24 inches deep. Wet ground. What size wire?

Will need two hot, one neutral, one ground.

Load will be lights, fan hot wTervheater on demand for one sink electric wall heater. No more than 60 amps at one time with all running. Thanks

Best Answer

At 125’ 4 awg copper would provide 1.79% voltage drop using 4 gauge wire would allow for 70 amp breaker in your main panel. Since this is detached you will want a ground rod also. To save on wire cost you could use #2 aluminum and still have 70a breaker at the main.

If you would like to play with wire sizes google southwire voltage drop calculator, that’s what I use the only part that’s not obvious is the box that asks for parallel sets put 1 it will give you the wire size and voltage drop info, it’s a handy tool.