Electrical – Wiring subpanel in detached garage

detached-structureelectrical-panel

Long time reader and first time poster here and want to make sure I'm running power to my detached garage properly.

I built a detached garage next to my house and just got done running the wires from the main meter panel to the subpanel inside the garage and the setup is a follows:

Main panel is approximately 125 feet from the subpanel. I have a total of 4 wires coming from the main: 2x 2awg aluminum wires connected to a double pole 125 amp breaker for hot, 1x 2awg aluminum wire connected to ground bar for neutral, 1x 4awg aluminum wire connected to ground bar for ground.

I have also installed 2 8' ground rods, hammered in 12 feet apart to provide a local ground for the garage with a solid 6awg copper wire in addition to the 4awg wire from the main panel.

I'm not going to bond the neutral bar to the subpanel chassis. And there will be another 125 amp breaker in the subpanel as the mail breaker for quick, local disconnect of all power.

This is my first time doing any wiring at this scope and level and want to make sure I'm not missing anything.

Thanks in advance,

Kash

Best Answer

A 125A "main breaker" in the subpanel is fine.

However, the breaker feeding this, which is in the main panel, must be 80A or 90A depending on the insulation of your wire.

Actually, I'd recommend a "larger" subpanel than 125A. The thing you really want is spaces, because a 90A subpanel can support a whole lot more circuits than you think it can. A whole lot more! A 30-space sub would not be excessive, and ones with that many spaces will tend to be 200A.

The old "16 spaces 32 circuits" trick doesn't work anymore, since almost all circuits these days require AFCI or GFCI breakers. NEC 2020 now requires it for 240V loads.

If you thought "125A breaker in the main panel is OK", then the source of your information is extremely poor - that's a hard mistake to make since every internet source will tell you otherwise. Revisit every one of your decisions which came from that data source.

Other than that, everything sounds OK, but 125A on #2Al is such a blunder that you should really go through the rest with a fine-tooth comb. Feel free to make full use of us!