Electrical Receptacle – Extending vs. Moving a 20 Amp Garage Outlet

necreceptacle

In attached garage there is a receptacle with a single 20 amp outlet (marked as "Freezer" in a breaker panel). It is in inconvenient location. The idea is to extend this circuit to an area where I need outlets. After it this circuit will power 5-6 outlets.

I found this in NEC 2017 [210.11 Branch Circuits Required (C) (4)]:

(4) Garage Branch Circuits. In addition to the number of
branch circuits required by other parts of this section, at least
one 120-volt, 20-ampere branch circuit shall be installed to
supply receptacle outlets in attached garages and in detached
garages with electric power. This circuit shall have no other
outlets.

Does it prevent me from extending this circuit? If yes – which options do I have? Either move or extend but add a new 20 amp circuit with a single outlet?

Best Answer

So long as all the outlets are in the garage, you meet the language of the code.